With out a panel rewire, a transformer with single phase output is the only option.
Everything needs to be fused accordingly, to the weakest link in the system, that would be the 225 amp panel or the wire feeding it. That panel is close to max load and does not have much room for expansion anyway. I believe you will already have a lug issue as you will need 4/0 wire or larger to feed it.
If planning for major expansion you need to build a larger distribution system, split it up and fuse accordingly, then feed a second panel for expansion.
Or go one step at a time, get this system working, then expand later at the 600 volt level with a second transformer.
Convert to 3 phase, rent the thing out for temp power when you don’t need it, might pay for the conversion.
one other option. rewind the stator in the genset.