Gas line trench depth to a garage

imdoo'n

Active VIP Member
Joined
Jan 15, 2008
Messages
58,430
Reaction score
51,887
Location
alberta from the back porch
a guy i know west of red deer had his house blow up west of red deer a few years ago, they were diggig in the yard and dug up the gas line, may have pulled on the line? anyway they left it till the next day, he went to work, and while on the way home for lunch, he saw a plume of smoke in the area of his house, his wife and kids escaped when the house started to shake, needless to say they got extremely lucky, point is gas at 4 0z pressure will explode,


call before ya dig, all the time. winter freeze and thaw moves utilies around in the excavated holes, till they pack down. be safe!
 

DaveB

Active VIP Member
Joined
Sep 18, 2007
Messages
5,946
Reaction score
17,074
Location
Red Deer area
hmm, seems like i get to mark it before you even show up. for what it is worth, first call will inform all members on there service that the caller requires utilities to be marked. as it stands now they will mark there lines to the meter on the power pole or on the house etc. secondary services from the house to garage or out buildings they will not do. and gas co-ops ad gas companies are not all marking lines past the meter, some do though. anyway put the line deeper, people forget where they are.

but you can do anything you like, as once it is buried "out of sight, out of mind".
When I built my fence, the First Call responders marked the power, phone and gas lines from my house to the detached garage, as well as the lines from the main to the meter.
 

maierch

Active VIP Member
Joined
Oct 26, 2008
Messages
1,565
Reaction score
2,512
Location
Calgary
Someone had to google it....

Frequently Asked Questions, Natural Gas Information, FAQ | Protech Plumbing

About halfway down the page... 18- 24". It also says that homeowners in the City of Calgary cannot obtain a gas permit only qualified gas fitters so you're going to have to do it in conjunction with a plumber anyways if you want to be in compliance with the bylaws.
 

imdoo'n

Active VIP Member
Joined
Jan 15, 2008
Messages
58,430
Reaction score
51,887
Location
alberta from the back porch
When I built my fence, the First Call responders marked the power, phone and gas lines from my house to the detached garage, as well as the lines from the main to the meter.

when did you build your fence dave? this has just been for the past year or so. telus, power are geerally not marking secondary services in most of the rural areas, and alot of the residential. mainly because homeowners have done the install and haven't hooked up the sheath grounds.
 

imdoo'n

Active VIP Member
Joined
Jan 15, 2008
Messages
58,430
Reaction score
51,887
Location
alberta from the back porch
Call the city to be sure, if it needs to be inspected by them. Really the only way to be sure. Would suck if it was 24 inches. Lol. Rent a hand operated trencher, put the line in a little deeper.
 

X-it

Active VIP Member
Joined
Jan 8, 2007
Messages
7,800
Reaction score
17,795
Location
Prince George
Codes are there for a reason. Just because you think it is better does not mean it is.
 

team dirt

Active VIP Member
Joined
Oct 17, 2008
Messages
2,150
Reaction score
5,886
Location
brooks ab/seymour arm
Website
www.sledseymourarm.ca
Codes are there for a reason. Just because you think it is better does not mean it is.

Code is just there for a minimum standard. It is not frowned upon to exceed code. Here is the section straight from the 149 gas code regarding burial. See the red writing for burial depth.

6.15 Underground piping and tubing6.15.1​
Piping having a nominal diameter of less than NPS 1/2 shall not be used underground.​
6.15.2​
Underground piping systems shall be joined or connected by welding or​
approved mechanicalcompression fittings.
6.15.3​
Underground tubing systems shall be joined or connected by brazing or​
approved mechanicalcompression or approved flared fittings.
6.15.4​

Piping and tubing shall be located neither less than 15 in (400 mm) underground nor less than 24 in(600 mm) under a commercial driveway or parking lot, except when it rises above ground at the point ofsupply to either a​

building or an outdoor appliance. Additional depth of cover shall be required wherethe piping is located in areas where physical damage is likely to occur, such as farm operations.
Δ​
B149.1-10​
© Canadian Standards Association
44​
January 2010
6.15.5​
A trench for underground piping or tubing shall be properly graded to prevent a sag in the piping ortubing.​
6.15.6​
Backfill material shall be free of sharp objects, large stones, or any other material that can damage thepiping or tubing.​
6.15.7​
Underground piping or tubing shall not pass below a foundation or wall, or under a​
building.
6.15.8​
Piping or tubing entering a​
building shall rise above grade before entry, unless otherwise permitted by the
authority having jurisdiction.​
6.15.9​
A watertight seal shall be provided at any point where piping or tubing passes through an outside wallbelow ground level.​
6.15.10​
When piping or tubing is laid under pavement and an entry to a​
building is made above ground level, asleeve shall be inserted to protect the piping or tubing where it comes through the pavement to permitfree movement of the soil and covering without placing strain on the piping or tubing.
6.15.11​
A vent pipe inspection point shall be installed adjacent to a​
building, either when the entire piping ortubing is covered with paving or when paving extends 25 ft (8 m) or more from the building, unless other
approved​
provisions have been made for venting the area surrounding the piping.
6.15.12​
An​
approved transition fitting shall be used for connecting piping or tubing of either steel or copper toplastic.
6.15.13​
The gas supply to underground plastic piping or tubing shall be controlled by a shut-off​
valve situatedabove ground.
6.15.14​
Plastic piping or tubing shall be accompanied by a tracing wire or other electronically detectable tracing​
media.
 
Last edited:

Joholio

Active VIP Member
Joined
Nov 20, 2012
Messages
35,161
Reaction score
29,699
Location
Hespero/Sicamous
Looks like its 18" min between maierch post and a couple friends in the business.

ImageUploadedByTapatalk1375910832.883886.jpg
 